Burning of the v/mA exit on ATR243
Posted: 13/10/2016, 15:35
Dear sirs,
We have a client that was trying to apply a ATR243-20ABC, to read the temperature of one process and to retransmit that process information to a PLC via the V/mA output.
The PLC only has a + terminal to connect the mA input signal.
According to the client the connections were made as follow:
Terminals 10 and 9 - 230 Vac;
Terminals 3, 2 and 1 - Probe connection (PT100 3 wires).
The parameters were set as follow:
C.out - C.01
Sen - PT
rETr - Ma.P
Lolr - -100
UPLr - 600
Jumper's JP5, JP6 and JP9 as explained in the manual (a with a free pin between the jumper 9 and the 5)
To check the output we connected one of probes of a multimeter to the ground and tried to mesure the mA on the terminal 4 with the other probe. The result was the burning of the circuit.
According to him, this was the correct way to measure the exit, but i have doubts.
Can you help us in order to explained to the client what went wrong?
Regards,
We have a client that was trying to apply a ATR243-20ABC, to read the temperature of one process and to retransmit that process information to a PLC via the V/mA output.
The PLC only has a + terminal to connect the mA input signal.
According to the client the connections were made as follow:
Terminals 10 and 9 - 230 Vac;
Terminals 3, 2 and 1 - Probe connection (PT100 3 wires).
The parameters were set as follow:
C.out - C.01
Sen - PT
rETr - Ma.P
Lolr - -100
UPLr - 600
Jumper's JP5, JP6 and JP9 as explained in the manual (a with a free pin between the jumper 9 and the 5)
To check the output we connected one of probes of a multimeter to the ground and tried to mesure the mA on the terminal 4 with the other probe. The result was the burning of the circuit.
According to him, this was the correct way to measure the exit, but i have doubts.
Can you help us in order to explained to the client what went wrong?
Regards,