Hey,
I am trying to achieve a system where my DRR245 mirror's its sensor 0-10v:
If the sensor sees 10v the output on SSR should be 0v.
If the sensor sees 0v the output on SSR should be 10v.
If the sensor sees 6v the output on SSR should be 4v.
Except when on the digital input sees 10v. Then it shoud be:
If the sensor sees 10v the output on SSR should be 4v. <- NOT 0
If the sensor sees 0v the output on SSR should be 10v.
The mirroring without the digital input was doable with following parameters:
C.out : C.01
SEn : 0.10
rETr : vo.P
Lol.r : 10
uPLi.r: 0
What should i do to enable the functions I need so that i can make the digital input part work?
[DDR245] 0-10v sensor and a digital input at the same time?
-
user13042
- Posts: 3
- Joined: 21/03/2016, 12:16
-
Pixsys tecnico 1
- Moderatore
- Posts: 1722
- Joined: 29/10/2010, 10:09
- Contact:
Re: [DDR245] 0-10v sensor and a digital input at the same ti
Hi,
with digital input you can switch from automatic/manual mode.When you are in manual mode you can select, using the arrows, how much the anologue output must generate.
with digital input you can switch from automatic/manual mode.When you are in manual mode you can select, using the arrows, how much the anologue output must generate.
-
user13042
- Posts: 3
- Joined: 21/03/2016, 12:16
Re: [DDR245] 0-10v sensor and a digital input at the same ti
Thanks for your quick reply.Pixsys tecnico 1 wrote:Hi,
with digital input you can switch from automatic/manual mode.When you are in manual mode you can select, using the arrows, how much the anologue output must generate.
The digital input will switch values a lot of times during the day. Must i update the output percentage or will it remember the setting?
I put 10v on the digital input i go to manual mode, change the percentage so that SSR goes from 4-10. Then i put 0v on the digital input it will automatically change the percentage back to 100 so that SSR goes from 0-10. Then when i put 10v on it again it will have remember the percentage i put it on so that SSR changes to 4-10 again.
Is that correct?
-
Pixsys tecnico 1
- Moderatore
- Posts: 1722
- Joined: 29/10/2010, 10:09
- Contact:
Re: [DDR245] 0-10v sensor and a digital input at the same ti
When you pass from automatic to manual, the regulatore mantains the last value, so if you have 7V on auto, when you pass to manual you will have 7V and then you can change using arrows.
-
HenryChind
- Posts: 6
- Joined: 03/02/2019, 19:08
- Location: Sri Lanka
- Contact:
DDR245 0 10v sensor and a digital input at the same time
When I open beta it auto finds my install directory and can load it no problems, except if you try to save in beta and play that save in the other one it will be odd.