ATR241-A

Posted: 20/01/2016, 19:32
by user12669
Hi.
I have an older model ATR241-A. I use it to regulate temperature but need a fan to come on when the alarm value is reached.I got this to happen but when the temperature falls below the alarm set point the fan stays on and should go off untill te alarm set point is reached again. Seems that the alarm does not auto reset and I hav no idea how to do this. How can I get this to happen?

Re: ATR241-A

Posted: 21/01/2016, 8:34
by Pixsys tecnico 1
Hi, check these parameters:
19 [cr.A] to "no.S"
21 [HYS] to "1" or "0"
30 [dELA] to "0"