[ATR401-22ABC-T] Controllo valvola modulante per metano

Post Reply
user1251
Posts: 2
Joined: 18/06/2011, 10:51

[ATR401-22ABC-T] Controllo valvola modulante per metano

Post by user1251 »

SONO UN ELETTRICISTA HO INSTALLATO QUESTO TERMOREGOLATORE ATR401-22ABC-T SU UN BRUCIATORE CON VALVOLA METANO MODULANTE.
PROVO A FARE UN ESEMPIO:
IMPOSTO LA TEMPERATURA A 570° PERCIÒ APPENA ACCENDO MI DEVE PARTIRE AL MASSIMO
DOPO DI CHE ARRIVATO A 570° DOVREBBE MODULARE SENZA SPEGNERE IL BRUCIATORE
MANTENENDO LA TEMPERATURA COSTANTE, COME SEGNALE HO USATO IL MORSETTO 9/10
CON USCITA IN VOLT DOPO AVERE PONTICELLATO IL JP3
QUELLO CHE CHIEDO COME FARE LA CONFIGURAZIONE PERCHÉ DAL LIBRETTO NON CIO'
CAPITO NIENTE MI SERVE UN AIUTINO GRAZIE
user1251
Posts: 2
Joined: 18/06/2011, 10:51

Re: CONFIGURAZIONE ATR401-22ABC-T

Post by user1251 »

HO PROVATO COME MI A DETTO AL TELEFONO, PERO IL C1 SI SPEGNE LA VALVOLA MOTORIZZATA VA AL MINIMO E LA TMPERATURA SALE SENZA SPEGNERE IL BRUCIATORE
CHE DOVREBBE AVERE UNA DIFFERENZA 5/6° DAL VALORE IMPOSTATO E IL Q1 NON INTERVIENE
AUTOMATICAMENTE
Pixsys tecnico 1
Moderatore
Posts: 1666
Joined: 29/10/2010, 10:09
Contact:

Re: CONFIGURAZIONE ATR401-22ABC-T

Post by Pixsys tecnico 1 »

Salve,
se il Q1 deve intervenire spegnendo il bruciatore se la temperatura supera di 5-6°C il set-point di lavoro, deve impostare quanto segue:
AL.1 : H.dAL
A1So : n.c.S
Come set-point di allarme deve impostare +5°C. In questo modo i contatti 3-5 sono chiusi finché non si supera il set di comando + 5°C. Al superamento di tale soglia, si aprono e spengono il bruciatore.