Hi,

My company bought a TD700 and we are trying to use its Modbus Master to read and write values with a Danfoss PLC (MCX).
Everything is OK I can read and write values but is it possible to create an edit field that can read an Modbus address on the danfoss PLC and write the same address ?
It seems that we need to create two variables in LogicLab one for reading and another for writing so in a edit field if I put the writing variable, if I change the setting on the danfoss PLC the writing variable is not updated :(

Eric
Pixsys tecnico 1
Moderatore
Posts: 1665
Joined: 29/10/2010, 10:09
Contact:

Re: TD700 Modbus Master

Post by Pixsys tecnico 1 »

Hi,
assign the same LogicLab variable as input and output to the same PLC address.
user10683
Posts: 51
Joined: 02/03/2015, 15:29

Re: TD700 Modbus Master

Post by user10683 »

Re,

Is it possible to request grouped modbus addresses ?

I have a lot of Modbus addresses so I need to group requests otherwise the modbus will be saturated.

Eric
Pixsys tecnico 1
Moderatore
Posts: 1665
Joined: 29/10/2010, 10:09
Contact:

Re: TD700 Modbus Master

Post by Pixsys tecnico 1 »

Hi,
you can group requests only with consecutively Modbus addresses using. For example,
if you add FC-03 function, you have to insert start address, then using ADD button you can add different address to reach with the same request (see attached image)
Immagine.png
You do not have the required permissions to view the files attached to this post.
user10683
Posts: 51
Joined: 02/03/2015, 15:29

Re: TD700 Modbus Master

Post by user10683 »

Hi,

OK I found how to do but I have a very BIG PROBLEM !

Modbus with a single PLC works very well but I have a big problem when 2 PLC's are connected to the same modbus network !

PLC 1 : modbus address 1
PLC 2 : modbus address 2

Modbus com : 19200 / RS485 / 8N1

Only one is working at the same time !

If I disconnect the first connector of the first PLC the second one starts to work adn vice-versa

Just a precision : my Modbus network works very well when I test with the software Modscan (I disconnect the connector on the TD700 and put it on my RS485 usb key).

I need a fast answer it is very important.
You do not have the required permissions to view the files attached to this post.
Pixsys tecnico 1
Moderatore
Posts: 1665
Joined: 29/10/2010, 10:09
Contact:

Re: TD700 Modbus Master

Post by Pixsys tecnico 1 »

Hi,
I cannot see if slave devices are good because they are custom and I do not have the PCT file. However, are you sure to have set slave 1 and salve 2 with different node number and different address number? see attached picture:
Cattura.PNG
You must have MODBUS ADDRESS and NODE NUMBER equals for each PLC, so:
PLC1: MODBUS ADDRESS= 1 and NODE NUMBER =1
PLC2: MODBUS ADDRESS= 2 and NODE NUMBER =2
You do not have the required permissions to view the files attached to this post.
user10683
Posts: 51
Joined: 02/03/2015, 15:29

Re: TD700 Modbus Master

Post by user10683 »

Sorry I send you a modified version my addresses are good when I test :

PLC1 : node number 1 modbus address 1
PLC2 : node number 2 modbus address 2
Pixsys tecnico 1
Moderatore
Posts: 1665
Joined: 29/10/2010, 10:09
Contact:

Re: TD700 Modbus Master

Post by Pixsys tecnico 1 »

HI, send my the entire project and also your custom device file so I can check all.

You can get it there:
C:\Program Files\Pixsys PC Tools\Catalog\ModbusCustom\
it will be a file named as the device ".PCT"
user10683
Posts: 51
Joined: 02/03/2015, 15:29

Re: TD700 Modbus Master

Post by user10683 »

I resend you my application test.

My PLC are now generic modbus devices but always the same issue.
You do not have the required permissions to view the files attached to this post.
Pixsys tecnico 1
Moderatore
Posts: 1665
Joined: 29/10/2010, 10:09
Contact:

Re: TD700 Modbus Master

Post by Pixsys tecnico 1 »

Try with this LogicLab project
TestLogicLab.zip
You do not have the required permissions to view the files attached to this post.