- Joined: 02/03/2015, 15:29
[TD700] Use as Modbus Master
Hi,
My company bought a TD700 and we are trying to use its Modbus Master to read and write values with a Danfoss PLC (MCX).
Everything is OK I can read and write values but is it possible to create an edit field that can read an Modbus address on the danfoss PLC and write the same address ?
It seems that we need to create two variables in LogicLab one for reading and another for writing so in a edit field if I put the writing variable, if I change the setting on the danfoss PLC the writing variable is not updated
Eric
My company bought a TD700 and we are trying to use its Modbus Master to read and write values with a Danfoss PLC (MCX).
Everything is OK I can read and write values but is it possible to create an edit field that can read an Modbus address on the danfoss PLC and write the same address ?
It seems that we need to create two variables in LogicLab one for reading and another for writing so in a edit field if I put the writing variable, if I change the setting on the danfoss PLC the writing variable is not updated
Eric
-
- Moderatore
- Posts: 1665
- Joined: 29/10/2010, 10:09
- Contact:
Re: TD700 Modbus Master
Hi,
assign the same LogicLab variable as input and output to the same PLC address.
assign the same LogicLab variable as input and output to the same PLC address.
-
- Posts: 51
- Joined: 02/03/2015, 15:29
Re: TD700 Modbus Master
Re,
Is it possible to request grouped modbus addresses ?
I have a lot of Modbus addresses so I need to group requests otherwise the modbus will be saturated.
Eric
Is it possible to request grouped modbus addresses ?
I have a lot of Modbus addresses so I need to group requests otherwise the modbus will be saturated.
Eric
-
- Moderatore
- Posts: 1665
- Joined: 29/10/2010, 10:09
- Contact:
Re: TD700 Modbus Master
Hi,
you can group requests only with consecutively Modbus addresses using. For example,
if you add FC-03 function, you have to insert start address, then using ADD button you can add different address to reach with the same request (see attached image)
you can group requests only with consecutively Modbus addresses using. For example,
if you add FC-03 function, you have to insert start address, then using ADD button you can add different address to reach with the same request (see attached image)
You do not have the required permissions to view the files attached to this post.
-
- Posts: 51
- Joined: 02/03/2015, 15:29
Re: TD700 Modbus Master
Hi,
OK I found how to do but I have a very BIG PROBLEM !
Modbus with a single PLC works very well but I have a big problem when 2 PLC's are connected to the same modbus network !
PLC 1 : modbus address 1
PLC 2 : modbus address 2
Modbus com : 19200 / RS485 / 8N1
Only one is working at the same time !
If I disconnect the first connector of the first PLC the second one starts to work adn vice-versa
Just a precision : my Modbus network works very well when I test with the software Modscan (I disconnect the connector on the TD700 and put it on my RS485 usb key).
I need a fast answer it is very important.
OK I found how to do but I have a very BIG PROBLEM !
Modbus with a single PLC works very well but I have a big problem when 2 PLC's are connected to the same modbus network !
PLC 1 : modbus address 1
PLC 2 : modbus address 2
Modbus com : 19200 / RS485 / 8N1
Only one is working at the same time !
If I disconnect the first connector of the first PLC the second one starts to work adn vice-versa
Just a precision : my Modbus network works very well when I test with the software Modscan (I disconnect the connector on the TD700 and put it on my RS485 usb key).
I need a fast answer it is very important.
You do not have the required permissions to view the files attached to this post.
-
- Moderatore
- Posts: 1665
- Joined: 29/10/2010, 10:09
- Contact:
Re: TD700 Modbus Master
Hi,
I cannot see if slave devices are good because they are custom and I do not have the PCT file. However, are you sure to have set slave 1 and salve 2 with different node number and different address number? see attached picture: You must have MODBUS ADDRESS and NODE NUMBER equals for each PLC, so:
PLC1: MODBUS ADDRESS= 1 and NODE NUMBER =1
PLC2: MODBUS ADDRESS= 2 and NODE NUMBER =2
I cannot see if slave devices are good because they are custom and I do not have the PCT file. However, are you sure to have set slave 1 and salve 2 with different node number and different address number? see attached picture: You must have MODBUS ADDRESS and NODE NUMBER equals for each PLC, so:
PLC1: MODBUS ADDRESS= 1 and NODE NUMBER =1
PLC2: MODBUS ADDRESS= 2 and NODE NUMBER =2
You do not have the required permissions to view the files attached to this post.
-
- Posts: 51
- Joined: 02/03/2015, 15:29
Re: TD700 Modbus Master
Sorry I send you a modified version my addresses are good when I test :
PLC1 : node number 1 modbus address 1
PLC2 : node number 2 modbus address 2
PLC1 : node number 1 modbus address 1
PLC2 : node number 2 modbus address 2
-
- Moderatore
- Posts: 1665
- Joined: 29/10/2010, 10:09
- Contact:
Re: TD700 Modbus Master
HI, send my the entire project and also your custom device file so I can check all.
You can get it there:
C:\Program Files\Pixsys PC Tools\Catalog\ModbusCustom\
it will be a file named as the device ".PCT"
You can get it there:
C:\Program Files\Pixsys PC Tools\Catalog\ModbusCustom\
it will be a file named as the device ".PCT"
-
- Posts: 51
- Joined: 02/03/2015, 15:29
Re: TD700 Modbus Master
I resend you my application test.
My PLC are now generic modbus devices but always the same issue.
My PLC are now generic modbus devices but always the same issue.
You do not have the required permissions to view the files attached to this post.
-
- Moderatore
- Posts: 1665
- Joined: 29/10/2010, 10:09
- Contact:
Re: TD700 Modbus Master
Try with this LogicLab project
You do not have the required permissions to view the files attached to this post.