Hi. yes, you were right, the temperature jumps with such difference temperature values when the output is switching on and off... how can I solve it??

Thank you.
Pixsys tecnico 1
Moderatore
Posts: 1662
Joined: 29/10/2010, 10:09
Contact:

Re: Temperature jumping

Post by Pixsys tecnico 1 »

Hi,
try to unplug outputs form the regulator. If temperature jumps anyway, the problem is in the regulator. If themperature is constant instead, the problem is in the heater element (maybe too "strong"), so Tuning function can help.
user9620
Posts: 9
Joined: 22/10/2014, 12:59

Re: Temperature jumping

Post by user9620 »

Hi.

I don't understand about the heater element. The output is connected to the contactor coil then the current cannot be high.... the output is not connected to the heater.


Regards.
Pixsys tecnico 1
Moderatore
Posts: 1662
Joined: 29/10/2010, 10:09
Contact:

Re: Temperature jumping

Post by Pixsys tecnico 1 »

If you disconnect the output, and when relay goes on and off the temperature jumps, the problem is in the regulator (maybe power supply failure) because no "power output" can modify the process.