Page 1 of 1

HOT TO AVOID E-05 WITH P100 ABOVE 140°C

Posted: 28/12/2010, 15:26
by Pixsys tecnico 1
Since PT100 is normally available with different measuring ranges, in most Pixsys controllers different ranges have been linearized and can be read correctly.
Therefore it is necessary to know the measuring range for the PT100 you are currently using and to set the controller accordingly.
Make sure about the measuring range of your PT100, enter configuration level (as descrive in User manual), go to parameter [SEN] and proceed as follows:

-For PT100 with restricted range (-200°..+140°) select option [Pt1]
-For PT100 with extended range (-200°..+600°) or if you are unable to source the correct range, select option [Pt]
-Exit configuration level and check the correct operation