ATR144 User Manual, Table of Configuration Parameters, (p74), section 12.I refers to GROUP L – Master Serial Port (only available on ATR144-ABC-T).
Using ATR144 front panel keyboard GROUP L is missing, or hidden? (Groups E and G are also missing). Is there a way to access this without using the Windows software?
Will try using My Pixsys app when I can get it to work.
ATR144-ABC-T master serial port section missing
-
Halsteads
- Posts: 14
- Joined: 30/04/2022, 16:49
ATR144-ABC-T master serial port section missing
You do not have the required permissions to view the files attached to this post.
-
Pixsys tecnico 1
- Moderatore
- Posts: 1738
- Joined: 29/10/2010, 10:09
- Contact:
Re: ATR144-ABC-T master serial port section missing
Hi,
can you tell us the firmware version of the controller?
You can see it during the powering of the controller, it is like "1.05"
can you tell us the firmware version of the controller?
You can see it during the powering of the controller, it is like "1.05"
-
Halsteads
- Posts: 14
- Joined: 30/04/2022, 16:49
Re: ATR144-ABC-T master serial port section missing
thanks,
firmware is 1.04
firmware is 1.04
-
Pixsys tecnico 1
- Moderatore
- Posts: 1738
- Joined: 29/10/2010, 10:09
- Contact:
Re: ATR144-ABC-T master serial port section missing
Hi,
group L is hidden if you have enable the "Slave mode" in the group K, parameter 149 "Mb.SL.".
You can try also to reset the configuration to factory default using "9999" password instead of "1234".
group L is hidden if you have enable the "Slave mode" in the group K, parameter 149 "Mb.SL.".
You can try also to reset the configuration to factory default using "9999" password instead of "1234".