PLC TCT500 Is not recognized

Post Reply
user13844
Posts: 1
Joined: 03/09/2016, 4:26

PLC TCT500 Is not recognized

Post by user13844 »

Hello, good afternoon, I have a problem with a TCT500, when entering with the PL.Prog4.75 software and trying to communicate with the PLC the message that appears is "Device does not answer", I have verified that the cable is in good condition. status because I have tried it with another device and it works. I have also tried updating firmware as indicated in viewtopic.php?t=2483, but I cannot connect to the PLC, some other solution?
I also see in the software an "Upgrade Boot Version" option, can that function be useful?
Pixsys tecnico 1
Moderatore
Posts: 1699
Joined: 29/10/2010, 10:09
Contact:

Re: PLC TCT500 Is not recognized

Post by Pixsys tecnico 1 »

Hi,
are you using a native RS232 or an USB-RS232 converter? If you use a converter, please check in the converter driver settings to configure the transmit delay as as lower as possible.