I would like to know how to upload PLC program from the TD410
upload programe from TD410
-
- Moderatore
- Posts: 1672
- Joined: 29/10/2010, 10:09
- Contact:
Re: upload programe from TD410
Hi,
to be able to upload the PLC code from a HMI, the source code of the project must be present in the HMi memory.
To be sure of that, the project must have this option enabled when it has been downloaded: otherwise the upload will not be possible.
If it was enabled, the upload is possible following these steps:
1- open the LogicLab editor and go to menu "File\Import Project form target"
2- in the popup window, select the type of PLC, in your case TD410_V3_PLC 3- Press "Configure Connection"
4- Select protocol "GDB" and press "Properties"
5- Configure the fields like the image below (change only the "IP address" value with the one of your PLC) 6- Press "Verify Connection" and if the result is positive, press "Upload Sources".
If the result is "Connection not available" the possible causes can be:
- Wrong IP address configuration or wrong ethernet connection in your PC (you are not able to "reach" the PLC).
- The source code is not available (present) in the HMI internal memory.
7- Choose a folder in your PC as destination folder and confirm
8- After the upload is finished, the folder will contains the project source code.
to be able to upload the PLC code from a HMI, the source code of the project must be present in the HMi memory.
To be sure of that, the project must have this option enabled when it has been downloaded: otherwise the upload will not be possible.
If it was enabled, the upload is possible following these steps:
1- open the LogicLab editor and go to menu "File\Import Project form target"
2- in the popup window, select the type of PLC, in your case TD410_V3_PLC 3- Press "Configure Connection"
4- Select protocol "GDB" and press "Properties"
5- Configure the fields like the image below (change only the "IP address" value with the one of your PLC) 6- Press "Verify Connection" and if the result is positive, press "Upload Sources".
If the result is "Connection not available" the possible causes can be:
- Wrong IP address configuration or wrong ethernet connection in your PC (you are not able to "reach" the PLC).
- The source code is not available (present) in the HMI internal memory.
7- Choose a folder in your PC as destination folder and confirm
8- After the upload is finished, the folder will contains the project source code.