Iris _

Pixsys Forum

everybody's effort for the same goal

ATR244-12ABC Wirring & Cofiguration With Transmitter

Post Reply
alirzab
Posts: 1
Joined: 11/12/2022, 8:27

ATR244-12ABC Wirring & Cofiguration With Transmitter

Post by alirzab »

Hello

Our company has purchased a device with ATR244-12ABC temperature controller. I want to keep the temperature of a tank at 25 degrees Celsius with this controller.
The temperature sensor is connected to a transmitter and produces a 4-20ma output that is connected to an input isolation amplifier(phoenix contact-2865340).
How the wiring of the controller and the settings of this circuit should be done.

Thank you!
Pixsys tecnico 6
Moderatore
Posts: 1218
Joined: 12/09/2016, 14:49

Re: ATR244-12ABC Wirring & Cofiguration With Transmitter

Post by Pixsys tecnico 6 »

Hi,
Attached the manual for ATR244.
If the 4-20ma signal is active, then already powered, you will need to connect it to pins 18-19 respecting the polarity of the wires.
If the 4-20ma signal is passive, then not powered, you will need to connect the positive wire to pin 16 (out 12/24V) and the negative wire (out 4-20ma) to the input of the ATR244 pin 19.

Here are the parameters to configure:
Group A [A.in.1]
- Par.1 [SEn.1] > "4-20"
- Par.4 [L.L.i.1] > "AI1 lower limit only for linear signals. Ex.: with input 4..20 mA this parameter takes value associated
to 4 mA. The value may be greater than the one entered on the next parameter."
- Par.5 [u.L.i.1] > "AI1 upper limit only for linear signals Ex: with input 4..20 mA this parameter takes value associated
to 20 mA. The value may be lower than the one entered on the previous parameter."

Best regards
You do not have the required permissions to view the files attached to this post.
Post Reply