Hello,
We aquired a controller ATR244-12ABC and we are trying to connect a flexible heating cord from Selecta with two connecting wires (https://grupo-selecta.com/productos/cor ... os-1000781). Could you indicate the corresponding connection positions based on the wiring diagram numbers? We tried to connect it on numbers 1 and 4.
However, something is off because the temperature goes up when the setpoint is lower than the measured temperature.
Thank you for your help.
Best regards,
Sofia
Heating cord connection to ATR244-12ABC
-
- Moderatore
- Posts: 1201
- Joined: 12/09/2016, 14:49
Re: Heating cord connection to ATR244-12ABC
Good morning,
The flexible heating cord must be connected to pins 4-5 for the heating function.
The connection have be as follows:
From pin 1 of the thermoregulator go to pin 4.
From Pin 5 connect to the heating cord.
From pin 2 of the thermoregulator connect to the second wire of the heating cord.
Best regards