Hello. I have ATR244-12ABC.
In user manual it is written, that relay outputs contacts are rated for 5A - 250 VAC resistive load.
Is it 5A - 250 VAC or 2A 230V as written in wiring diagrams?

If controller is used for driving motorized valve with 24VAC 50-60 Hz motor, is it correct application? As far as I understand, motors have inductive load, not resistive. Motor is connected to pins 3, 4 and 5 for cooling function only, no heating (par 35: c.Val, and par 38: cooL). For ON/OFF function (no PID) it seems to work.