ATR111

Post by Faulheim »

Good day,

Can you please assist with the following programming on ATR111.
Is there a way to set temp. let’s say to 5degrees off and then again on 8 degrees on. This will be for a fridge to keep temp between 5 and 8 degrees.

Thank you in advanced.
Regards
Francois
Pixsys tecnico 6
Moderatore
Posts: 1201
Joined: 12/09/2016, 14:49

Re: ATR111

Post by Pixsys tecnico 6 »

Good morning,
You will need to set the OUT1 set point to 5°C and set to Par.14 [HY.c] at 3°C.
the regulator will adjust between 5 and 8 degrees .
The regulation will be made from OUT1 PIN 4-5.

Best Regards
Faulheim
Posts: 3
Joined: 16/03/2022, 11:40

Re: ATR111

Post by Faulheim »

Thank you so much. Appreciate
Faulheim
Posts: 3
Joined: 16/03/2022, 11:40

Re: ATR111

Post by Faulheim »

Pixsys tecnico 6 wrote:Good morning,
You will need to set the OUT1 set point to 5°C and set to Par.14 [HY.c] at 3°C.
the regulator will adjust between 5 and 8 degrees .
The regulation will be made from OUT1 PIN 4-5.

Best Regards
The moment that i set the HY.c to 3 Degrees it doesn,t switch of or on at 5 degrees. Only when parameter is set to 00 in HY.c
Pixsys tecnico 6
Moderatore
Posts: 1201
Joined: 12/09/2016, 14:49

Re: ATR111

Post by Pixsys tecnico 6 »

If the regulation is to be made in "cold", set Par.11 [Reg.] to "coo".
in the Par.14 [HY. c] must be set the band in which the regulator does not perform any function, then it will activate the output exceeded 8°C and turn off the output when reaching 5°C.

Best Regards