PL110 software reset
-
- Posts: 4
- Joined: 10/04/2011, 8:41
PL110 software reset
I am facing an issue with PL110 that causes it to reset with random intervals. What are potential reasons for this type of behavior?
-
- Moderatore
- Posts: 1671
- Joined: 29/10/2010, 10:09
- Contact:
Re: PL110 software reset
Are you using interrupt?
Are you usin C code?
Can you attach you PLC software?
Are you usin C code?
Can you attach you PLC software?
-
- Posts: 4
- Joined: 10/04/2011, 8:41
Re: PL110 software reset
Thank you for the reply. Interrupt (100ms) with software PID update is in use and it seems that problems relate to this combo. I couldn't attach the the full code put it seems this single line (on 100ms interrupt) causes the problem.
You do not have the required permissions to view the files attached to this post.
-
- Moderatore
- Posts: 1671
- Joined: 29/10/2010, 10:09
- Contact:
Re: PL110 software reset
Ok,
please try this:
eliminate this line on the interrupt, and put the same line in the main code, using a timer to "scan" the code every 100mS.
Do you have some errors reported by SM1?
please try this:
eliminate this line on the interrupt, and put the same line in the main code, using a timer to "scan" the code every 100mS.
Do you have some errors reported by SM1?