Movicon Alarm
-
user14306
- Posts: 20
- Joined: 01/12/2016, 13:51
Movicon Alarm
Hello, I have a little problem with my TD810 I can't get the sound when an alarm goes off.
-
Pixsys tecnico 6
- Moderatore
- Posts: 1212
- Joined: 12/09/2016, 14:49
Re: Movicon Alarm
Hello,
Can you better specify your application and your TD810 issue?
Best regards.
Can you better specify your application and your TD810 issue?
Best regards.
-
user14306
- Posts: 20
- Joined: 01/12/2016, 13:51
Re: Movicon Alarm
Hello,
When an alarm goes off, I can't get any sound coming out of the HMI.
While when I press the screen there is a "beep" coming out of the HMI.
When an alarm goes off, I can't get any sound coming out of the HMI.
While when I press the screen there is a "beep" coming out of the HMI.
-
user14306
- Posts: 20
- Joined: 01/12/2016, 13:51
Re: Movicon Alarm
My program is that when a controller alarm is triggered, an alarm window will appear on the HMI. But I don't get any sound coming out of the HMI.
-
Pixsys tecnico 6
- Moderatore
- Posts: 1212
- Joined: 12/09/2016, 14:49
Re: Movicon Alarm
Hi,
the beep sound is a system sound of the HMI buzzer, but Movicon can't manage the HMI buzzer. The HMI buzzer works only for the touch screen and it is not available for the Movicon software. If you need a sound when the alarm is active, you need an external buzzert that you can activate by the HMI. Usually an external buzer is activate by a digital output of a PLC I/O MOdule.
The IO module link below:
https://www.pixsys.net/en/products/plcs ... es/etd1644
https://www.pixsys.net/en/products/plcs ... es/mcm260x
Best regards.
the beep sound is a system sound of the HMI buzzer, but Movicon can't manage the HMI buzzer. The HMI buzzer works only for the touch screen and it is not available for the Movicon software. If you need a sound when the alarm is active, you need an external buzzert that you can activate by the HMI. Usually an external buzer is activate by a digital output of a PLC I/O MOdule.
The IO module link below:
https://www.pixsys.net/en/products/plcs ... es/etd1644
https://www.pixsys.net/en/products/plcs ... es/mcm260x
Best regards.