I programmed the parameters up to 999 degrees and when the temperature reaches 360 degrees back down to 0.
If anyone can help me, thank you
ATR121 temperature up to 999 degrees
-
Pixsys tecnico 6
- Moderatore
- Posts: 1212
- Joined: 12/09/2016, 14:49
Re: ATR121 temperature up to 999 degrees
Hi,
what parameters has it changed compared to the default options? Please can you post a parameter list? Please, can you explain your application?
Best Regards.
what parameters has it changed compared to the default options? Please can you post a parameter list? Please, can you explain your application?
Best Regards.
-
maismar
- Posts: 4
- Joined: 20/02/2019, 1:49
Re: ATR121 temperature up to 999 degrees
c.ou o 1.2 t.c. 0
SEn tc.j AL. A.A
d.p. 0 c.r.A n.o.S
Lo.S 0 S.c.A. c.o.
HI.S 999 Ld2 c.c.
Lo.n 0 HY.A 0.0
HI.n. 999 dE.A 0
Lat Off P.SE. FrE
cA.o 0.0 FiL 10
cA.G 0.0 tun off
rEG. HEA Fnc d.SE
S.c.c. c.o. GrA ºC
Ld1 c.c. coF Air
HY.c 0.0 P.b.N 1.00
P.b. 0 aud 0
t.i. 0 t.c.2 10
t.d. 0 FL.u off
I'm using it to show the tempura of an oven with tempura up to 750 degrees.
SEn tc.j AL. A.A
d.p. 0 c.r.A n.o.S
Lo.S 0 S.c.A. c.o.
HI.S 999 Ld2 c.c.
Lo.n 0 HY.A 0.0
HI.n. 999 dE.A 0
Lat Off P.SE. FrE
cA.o 0.0 FiL 10
cA.G 0.0 tun off
rEG. HEA Fnc d.SE
S.c.c. c.o. GrA ºC
Ld1 c.c. coF Air
HY.c 0.0 P.b.N 1.00
P.b. 0 aud 0
t.i. 0 t.c.2 10
t.d. 0 FL.u off
I'm using it to show the tempura of an oven with tempura up to 750 degrees.
-
maismar
- Posts: 4
- Joined: 20/02/2019, 1:49
Re: ATR121 temperature up to 999 degrees
I'm using it to show the tempura of an oven with tempura up to 750 degrees.
see the Attach
see the Attach
You do not have the required permissions to view the files attached to this post.
-
Pixsys tecnico 6
- Moderatore
- Posts: 1212
- Joined: 12/09/2016, 14:49
Re: ATR121 temperature up to 999 degrees
Hi,
we think there is a probe issue. What type of probe are you using? Are you sure it is a TC-J? If you are using a TC-J probe you don't need to change the default value of the parameters [Lo.n] and [Hi.n].
Best Regards
we think there is a probe issue. What type of probe are you using? Are you sure it is a TC-J? If you are using a TC-J probe you don't need to change the default value of the parameters [Lo.n] and [Hi.n].
Best Regards
-
maismar
- Posts: 4
- Joined: 20/02/2019, 1:49
Re: ATR121 temperature up to 999 degrees
I think it is a probe type J 6x100 mm
At least that's what it says on the invoice
I'm calling posts 11 and 12
Best regard
At least that's what it says on the invoice
I'm calling posts 11 and 12
Best regard
-
Pixsys tecnico 6
- Moderatore
- Posts: 1212
- Joined: 12/09/2016, 14:49
Re: ATR121 temperature up to 999 degrees
Hi,
your electrical wire connections are right if you are using a Tc-j. Are you sure your tc-j is working fine? Did you try to use another tc-j?
Best regards.
your electrical wire connections are right if you are using a Tc-j. Are you sure your tc-j is working fine? Did you try to use another tc-j?
Best regards.