Iris _

Pixsys Forum

everybody's effort for the same goal

ATR121 temperature up to 999 degrees

Post Reply
maismar
Posts: 4
Joined: 20/02/2019, 1:49

ATR121 temperature up to 999 degrees

Post by maismar »

I programmed the parameters up to 999 degrees and when the temperature reaches 360 degrees back down to 0.
If anyone can help me, thank you
Pixsys tecnico 6
Moderatore
Posts: 1201
Joined: 12/09/2016, 14:49

Re: ATR121 temperature up to 999 degrees

Post by Pixsys tecnico 6 »

Hi,
what parameters has it changed compared to the default options? Please can you post a parameter list? Please, can you explain your application?

Best Regards.
maismar
Posts: 4
Joined: 20/02/2019, 1:49

Re: ATR121 temperature up to 999 degrees

Post by maismar »

c.ou o 1.2 t.c. 0
SEn tc.j AL. A.A
d.p. 0 c.r.A n.o.S
Lo.S 0 S.c.A. c.o.
HI.S 999 Ld2 c.c.
Lo.n 0 HY.A 0.0
HI.n. 999 dE.A 0
Lat Off P.SE. FrE
cA.o 0.0 FiL 10
cA.G 0.0 tun off
rEG. HEA Fnc d.SE
S.c.c. c.o. GrA ºC
Ld1 c.c. coF Air
HY.c 0.0 P.b.N 1.00
P.b. 0 aud 0
t.i. 0 t.c.2 10
t.d. 0 FL.u off

I'm using it to show the tempura of an oven with tempura up to 750 degrees.
maismar
Posts: 4
Joined: 20/02/2019, 1:49

Re: ATR121 temperature up to 999 degrees

Post by maismar »

I'm using it to show the tempura of an oven with tempura up to 750 degrees.

see the Attach
You do not have the required permissions to view the files attached to this post.
Pixsys tecnico 6
Moderatore
Posts: 1201
Joined: 12/09/2016, 14:49

Re: ATR121 temperature up to 999 degrees

Post by Pixsys tecnico 6 »

Hi,
we think there is a probe issue. What type of probe are you using? Are you sure it is a TC-J? If you are using a TC-J probe you don't need to change the default value of the parameters [Lo.n] and [Hi.n].

Best Regards
maismar
Posts: 4
Joined: 20/02/2019, 1:49

Re: ATR121 temperature up to 999 degrees

Post by maismar »

I think it is a probe type J 6x100 mm
At least that's what it says on the invoice
I'm calling posts 11 and 12

Best regard
Pixsys tecnico 6
Moderatore
Posts: 1201
Joined: 12/09/2016, 14:49

Re: ATR121 temperature up to 999 degrees

Post by Pixsys tecnico 6 »

Hi,
your electrical wire connections are right if you are using a Tc-j. Are you sure your tc-j is working fine? Did you try to use another tc-j?

Best regards.
Post Reply