Iris _

Pixsys Forum

everybody's effort for the same goal

TD240 Master & Slave

Post Reply
RamonGC
Posts: 3
Joined: 22/01/2019, 19:29

TD240 Master & Slave

Post by RamonGC »

Hello, I'm using a TD240 as a master device in a modbus network with VFDs as slave devices.
My customer wants to integrate the system to a PLC they already have but the PLC is a Master device in another modbus network. Is there a way i can communicate the TD240 as a master device with a 3rd party PLC as a master device too?
I also have a EPL101 that i can use as an interface if needed.
Pixsys tecnico 6
Moderatore
Posts: 1184
Joined: 12/09/2016, 14:49

Re: TD240 Master & Slave

Post by Pixsys tecnico 6 »

Hi,
it is possible if you use the EXP1 as Master mode and COM2 as Slave mode, but you need use the RS232 for the COM2.
TD240_Master_Slave.PNG
Best Regards.
You do not have the required permissions to view the files attached to this post.
Post Reply