hello
i want to store the actual temperature via labview (5V). therefore i put the jumper on jp3. but then i only get 0.011 V altough the temperature is increasing.
any ideas?
[ATR401-22ABC-T] AO in Volt
-
- Moderatore
- Posts: 1665
- Joined: 29/10/2010, 10:09
- Contact:
Re: AO in Volt - ATR401-22ABC-T
Hi,
if you want to retransmit the input signal in volt 0-10V, you have to set the following parameters:
[Sen] set the type of sensor
[rEtr] "Pro.1"
[LoLr] and [uPLr] as the lower and the upper limits for analog output for example:
Temperature form 0°C to 100°C --> 0V to 10V, [LoLr]:"0" and [uPLr]: "100"
You have also to put the jumper on jp3.
if you want to retransmit the input signal in volt 0-10V, you have to set the following parameters:
[Sen] set the type of sensor
[rEtr] "Pro.1"
[LoLr] and [uPLr] as the lower and the upper limits for analog output for example:
Temperature form 0°C to 100°C --> 0V to 10V, [LoLr]:"0" and [uPLr]: "100"
You have also to put the jumper on jp3.
-
- Posts: 6
- Joined: 04/01/2012, 10:15
Re: AO in Volt - ATR401-22ABC-T
thanks... works perfect!