Standard procedure to configure the correct sensor and avoid error E-5:
-Press FNC keyfor 3 seconds (SET key for ATR243-DRR245 series)
-Pressing arrow keys change the digit flashing, press SET key to pass to the next digit
-Enter the password "1234" ("123" for ATR121 series), press SET to confirm the last digit
-Scroll the parameters list using arrow Keys
-Go to the second parameter [SEN]
-Holding SET key, use arrows to scroll the sensors list
-Relase SET key when you see the correct sensor connected
-The confirmation of the configuration is made by pressing FNC key (both arrows key for ATR243-DRR245 series)
Now you will see on the display the correct temperature value.
HOW TO AVOID E-5 ERROR
-
- Moderatore
- Posts: 1716
- Joined: 29/10/2010, 10:09
- Contact:
Jump to
- Forum Italiano
- ↳ Argomenti Generali
- ↳ FAQ Regolatori e Termoregolatori
- ↳ FAQ Controllori di processo / Programmatori a step
- ↳ FAQ PLC, HMi e Interfacce
- ↳ HMI LogicLab - Movicon (TD410, TD710, TD810, TD820)
- ↳ PLC LogicLab (PL280, PL500, PL600)
- ↳ PLC e HMI Codesys (PL700, TC6xx, TC8xx)
- ↳ PanelPC (PC800, PC815, PC820, PC830)
- ↳ WebPanel (WPxxx)
- ↳ Moduli I/O e convertitori
- ↳ PLC e HMI PlProg - TdDesigner (EPL101, PL250, PL260, TD240, TD320)
- ↳ HMI LogicLab - PageLab (TDxxx, TY5xx, TY7xx)
- ↳ FAQ sonde e ssr
- ↳ FAQ Timer / Contatori / Tachimetri
- ↳ FAQ Inverter
- English Forum
- ↳ General Topics
- ↳ FAQ controllers
- ↳ FAQ Process controllers / Steps controllers
- ↳ FAQ PLC, HMI and Interfaces
- ↳ HMI LogicLab - Movicon (TD410, TD710, TD810, TD820)
- ↳ PLC LogicLab (PL280, PL500, PL600)
- ↳ PLC and HMI Codesys (PL700, TC6xx, TC8xx)
- ↳ PanelPC (PC800, PC815, PC820, PC830)
- ↳ WebPanel (WPxxx)
- ↳ I/O modules and converters
- ↳ PLC and HMI PlProg - TdDesigner (EPL101, PL250, PL260, TD240, TD320)
- ↳ HMI LogicLab - PageLab (TDxxx, TY5xx, TY7xx)
- ↳ FAQ sensors and SSR
- ↳ FAQ Timers / Counters / Tachometers
- ↳ FAQ Inverter