Hello,
Could you please explain by a simple example what is parameter HY.C (dead band with ATR 121 in PID) meaning/ purpose? Also what is the difference between rEG = HEA and rEG = H.o.o?
Thx
ATR 121 in PID, HyC (dead band), H.o.o parameter meaning
-
user10989
- Posts: 9
- Joined: 16/04/2015, 13:59
-
Pixsys tecnico 6
- Moderatore
- Posts: 1218
- Joined: 12/09/2016, 14:49
Re: ATR 121 in PID, HyC (dead band), H.o.o parameter meaning
Hi,
the Hy.C parameter is the Hysteresis if you use ON/OFF regulation mode. If you use PID regulation mode Hy.C is the Dead Band.
If you set the REG parameterer as HEA, the command output is ON under your setpoint (ON/OFF mode), but if you use PID the Proportional Band is centered on the setpoint. If you set REG as H.o.o. (using PID mode) when the temperature is over the Setpoint the command output is OFF.
Best Regards
the Hy.C parameter is the Hysteresis if you use ON/OFF regulation mode. If you use PID regulation mode Hy.C is the Dead Band.
If you set the REG parameterer as HEA, the command output is ON under your setpoint (ON/OFF mode), but if you use PID the Proportional Band is centered on the setpoint. If you set REG as H.o.o. (using PID mode) when the temperature is over the Setpoint the command output is OFF.
Best Regards
-
user10989
- Posts: 9
- Joined: 16/04/2015, 13:59
Re: ATR 121 in PID, HyC (dead band), H.o.o parameter meaning
Yes, thanks a lot. Just one more thing. If the process is heating ONLY (no cooling) with oil as heating fluid, do you advise to set parameter 33. (cooling fluid) c.o.F to Oil or leave it Air by default?
Regards
Regards
-
Pixsys tecnico 6
- Moderatore
- Posts: 1218
- Joined: 12/09/2016, 14:49
Re: ATR 121 in PID, HyC (dead band), H.o.o parameter meaning
Hi,
leave it by default value.
Best Regards.
leave it by default value.
Best Regards.