Hi,
I have a PL260 with a third party SCADA application running polling on the EXP1 port. Whenever I try to poll more than 20 registers the PLC does not respond healthily (4x0001 - 4x0020 works, 4x0001 - 4x0021 does not work - N.B. I'm not using VW0 aka 4x0000). I have tried 'Modbus Poll' as well and the same result occurs.
Is there a limitation for any reason, I didn't see anything in the user manual?
Regards
Modbus/RTU polling data from PL260
-
- Moderatore
- Posts: 1665
- Joined: 29/10/2010, 10:09
- Contact:
Re: Modbus/RTU polling data from PL260
Hi,
you can do a multi-reading up to 16 consecutive words. Then you must send a new Modbus reading package
you can do a multi-reading up to 16 consecutive words. Then you must send a new Modbus reading package