Possible to use DI to change Lo.L.r. ?

Post by user13042 »

Hello,

Parameters i am using at the moment:
c.out c.o.1
Sen. 0.10
P.b. 27
t.i. 14,1
t.d. 3,5
S.d.tu. 100
oP.Mo. Pr.cY
rEtr vo.P
Lo.L.r. 1000
uP.L.r. 0

What I can do NOW:
Analog in = 0v, SSR out = 10v
Analog in = 1v, SSR out = 9v
Analog in = 2v, SSR out = 8v
Analog in = 3v, SSR out = 7v
Analog in = 4v, SSR out = 6v
Analog in = 5v, SSR out = 5v
Analog in = 6v, SSR out = 4v
Analog in = 7v, SSR out = 3v
Analog in = 8v, SSR out = 2v
Analog in = 9v, SSR out = 1v
Analog in = 10v, SSR out = 0v

What I want:
DI = 0v
Analog in = 0v, SSR out = 10v
Analog in = 1v, SSR out = 9v
Analog in = 2v, SSR out = 8v
Analog in = 3v, SSR out = 7v
Analog in = 4v, SSR out = 6v
Analog in = 5v, SSR out = 5v
Analog in = 6v, SSR out = 4v
Analog in = 7v, SSR out = 3v
Analog in = 8v, SSR out = 2v
Analog in = 9v, SSR out = 1v
Analog in = 10v, SSR out = 0v

DI = 10v
Analog in = 0v, SSR out = 6v
Analog in = 1v, SSR out = 5.4v
Analog in = 2v, SSR out = 4.8v
Analog in = 3v, SSR out = 4.2v
Analog in = 4v, SSR out = 3.6v
Analog in = 5v, SSR out = 3.0v
Analog in = 6v, SSR out = 2.4v
Analog in = 7v, SSR out = 1.8v
Analog in = 8v, SSR out = 1.2v
Analog in = 9v, SSR out = 0.6v
Analog in = 10v, SSR out = 0v

I think I can achieve this if the DI can change the LO.L.r ?

If there is 0v on the DI the LO.L.r should be 1000.
If there is 10v on the DI the LO.L.r should be 600.

Or should the DI change another parameter?

Please advice me what parameter I should change.

Thanks in advance,
Pim
Pixsys tecnico 1
Moderatore
Posts: 1738
Joined: 29/10/2010, 10:09
Contact:

Re: Possible to use DI to change Lo.L.r. ?

Post by Pixsys tecnico 1 »

Hi,
output parameters cannot be change with DI, only by parameters.
You can change regulation type instead (output 0%->100% or 100%->0%) using D.I.
You can do this only using ATR401 series.