I am trying to get my laptop to communicate with TD900 HMI panel.What is the procedure for setting IP addresses to communicate?
LAPTOP TO TD900 ETHERNET CONNECTION
-
- Moderatore
- Posts: 1665
- Joined: 29/10/2010, 10:09
- Contact:
Re: LAPTOP TO TD900 ETHERNET CONNECTION
Hi,
set fixed IP address for both computers (not DHCP).
If you want to connect LogicLab/PageLab to TD900 HMI, you hsve to run LLExec.exe from "D:\LLExec\" before (TD900 HMI will become black).
set fixed IP address for both computers (not DHCP).
If you want to connect LogicLab/PageLab to TD900 HMI, you hsve to run LLExec.exe from "D:\LLExec\" before (TD900 HMI will become black).
-
- Posts: 3
- Joined: 16/09/2015, 23:41
Pagelab printing
I am having trouble printing from Pagelab. I want each page on a full A4 size sheet, i have tried changing the printer settings but it still remains very small on the top left side of the page.
How can i change the printer settings within pagelab?
How can i change the printer settings within pagelab?
-
- Moderatore
- Posts: 1665
- Joined: 29/10/2010, 10:09
- Contact:
Re: LAPTOP TO TD900 ETHERNET CONNECTION
Hi,
you can generate the documentation using this function Then you can go to the project's directory and in the folder "docImages" you will find all sinoptic's images at full resolution.
you can generate the documentation using this function Then you can go to the project's directory and in the folder "docImages" you will find all sinoptic's images at full resolution.
You do not have the required permissions to view the files attached to this post.
-
- Posts: 26
- Joined: 27/05/2019, 23:11
TD900 with two seperate Modbus networks.
Hi,
I would like to setup a TD900 panel PC with two seperate Modbus Networks.
Do you have a setup procedure for it?
I know that the master is RTU on com 4, the second is Com 1 RS232 using an inverter from RS485 to Rs232.
Is this correct?
Will this allow me to increase the number of nodes that can be connected to the HMI?
I would like to setup a TD900 panel PC with two seperate Modbus Networks.
Do you have a setup procedure for it?
I know that the master is RTU on com 4, the second is Com 1 RS232 using an inverter from RS485 to Rs232.
Is this correct?
Will this allow me to increase the number of nodes that can be connected to the HMI?
-
- Moderatore
- Posts: 1188
- Joined: 12/09/2016, 14:49
Re: LAPTOP TO TD900 ETHERNET CONNECTION
Hi,
the TD900 hardware allows a single Modbus RTU Master. You can use the RS485 or the RS232 connection, but not both.
Best Regards.
the TD900 hardware allows a single Modbus RTU Master. You can use the RS485 or the RS232 connection, but not both.
Best Regards.
-
- Posts: 26
- Joined: 27/05/2019, 23:11
Re: LAPTOP TO TD900 ETHERNET CONNECTION
How is the Modbus TCP/IP setup?
it has a Generic Modus which im not sure about the set up procedure?
Do ye have the procedure for download?
it has a Generic Modus which im not sure about the set up procedure?
Do ye have the procedure for download?
-
- Moderatore
- Posts: 1188
- Joined: 12/09/2016, 14:49
Re: LAPTOP TO TD900 ETHERNET CONNECTION
Hi,
please check the example number 6 al follow link:
https://forum.pixsys.net/viewtopic.php?f=25&t=2231
It explains how to configure the "Status variable" and the Modbus TCP/IP using LogicLab software (same using TD900).
Best Regards.
please check the example number 6 al follow link:
https://forum.pixsys.net/viewtopic.php?f=25&t=2231
It explains how to configure the "Status variable" and the Modbus TCP/IP using LogicLab software (same using TD900).
Best Regards.