Post by user967 »

i have this error on display on power up , the T/C is ok (type K)..but i am usinga 10 meter compensating cable.. any ideas anyone??
Pixsys tecnico 1
Moderatore
Posts: 1666
Joined: 29/10/2010, 10:09
Contact:

Re: i have error E-5 on display

Post by Pixsys tecnico 1 »

What controller do you use?
Check the polarity of the thermocouple and the connections to the controllers. If the error doesn't disappear try to short-circuit the thermocouple input: you should see a temperature around 20°C.
user967
Posts: 2
Joined: 21/04/2011, 16:41

Re: i have error E-5 on display

Post by user967 »

its a ATR121-AD controller..
first time we have used these..if i short the input its ok. any more ideas i can try?
Pixsys tecnico 1
Moderatore
Posts: 1666
Joined: 29/10/2010, 10:09
Contact:

Re: i have error E-5 on display

Post by Pixsys tecnico 1 »

It seems the thermocouple is badly connected or broken. Try to change it.