[TCT101-2ABC] with prescale value
-
- Posts: 36
- Joined: 09/02/2011, 14:33
- Location: Latvia
- Contact:
[TCT101-2ABC] with prescale value
Ciao!
One more question!
I need to count signals! But with prescale value !
For example i got 10 impulse , that i need to show as 1L and i need to count 10L and turn output off!
Can i do this with TCT101-2ABC (Counter)? ( i mean prescale )
Because i can not find a prescale value parameter!
Thank You in advance!
Martins
One more question!
I need to count signals! But with prescale value !
For example i got 10 impulse , that i need to show as 1L and i need to count 10L and turn output off!
Can i do this with TCT101-2ABC (Counter)? ( i mean prescale )
Because i can not find a prescale value parameter!
Thank You in advance!
Martins
-
- Moderatore
- Posts: 1671
- Joined: 29/10/2010, 10:09
- Contact:
Re: TCT101
Yes of course!
Using the TCT101-2ABC you can set the input and visualized counts in the "inc.1" and "uiC.1" parameters.
In your example you have to set:
[inC.1]: "10" (inputs counted)
[uiC.1]: "1" (inputs visualized)
[out1]: "C.1nc" (relay closes after reaching setpoint)
To modify the set-point value you have to go out of the parameters and use the arrows (the value is shown on the red display).
Using the TCT101-2ABC you can set the input and visualized counts in the "inc.1" and "uiC.1" parameters.
In your example you have to set:
[inC.1]: "10" (inputs counted)
[uiC.1]: "1" (inputs visualized)
[out1]: "C.1nc" (relay closes after reaching setpoint)
To modify the set-point value you have to go out of the parameters and use the arrows (the value is shown on the red display).
-
- Posts: 36
- Joined: 09/02/2011, 14:33
- Location: Latvia
- Contact:
Re: [TCT101-2ABC] with prescale value
Ciao!
Can i use TCT101-2ABC:
We need to count impulses from encoder! When we get our set point (for example 400 impulses ), the output turns to ON and is active for dT ( that i can change , max 2 sec ),
After that controller returns to counting mode and starts from 0 again to set point!
Example:
We need to count 400 impulses, then turn output on for 1,5sec., and restart counting from zero and start again!
Is that time holding possible?
Can i use TCT101-2ABC:
We need to count impulses from encoder! When we get our set point (for example 400 impulses ), the output turns to ON and is active for dT ( that i can change , max 2 sec ),
After that controller returns to counting mode and starts from 0 again to set point!
Example:
We need to count 400 impulses, then turn output on for 1,5sec., and restart counting from zero and start again!
Is that time holding possible?
-
- Moderatore
- Posts: 1671
- Joined: 29/10/2010, 10:09
- Contact:
Re: [TCT101-2ABC] with prescale value
Yes,
you can easily set the "output duration" with [A.L.c.1] and [C.o.N.1] parameters.
you can easily set the "output duration" with [A.L.c.1] and [C.o.N.1] parameters.
-
- Posts: 36
- Joined: 09/02/2011, 14:33
- Location: Latvia
- Contact:
Re: [TCT101-2ABC] with prescale value
Ciao,
thank You for answer!
But can i disable input, while is output duration in time?
So that we count till setpoint, then output start to work for duration time, but in this time the counter doesnt count. It start to count again after the duration time ends.
thank You for answer!
But can i disable input, while is output duration in time?
So that we count till setpoint, then output start to work for duration time, but in this time the counter doesnt count. It start to count again after the duration time ends.
-
- Moderatore
- Posts: 1671
- Joined: 29/10/2010, 10:09
- Contact:
Re: [TCT101-2ABC] with prescale value
You can't stop the counting but using the [A.L.c.1] parameter you set when the counting restarts/resets.
For example, if you set [A.L.c.1] as "s.o.d.1" the counting restarts if "counter = Set1 + Output Duration 1" where "Output Duration 1" is the time during the relay is active.
For example, if you set [A.L.c.1] as "s.o.d.1" the counting restarts if "counter = Set1 + Output Duration 1" where "Output Duration 1" is the time during the relay is active.
-
- Posts: 36
- Joined: 09/02/2011, 14:33
- Location: Latvia
- Contact:
Re: [TCT101-2ABC] with prescale value
Ciao!
What is max counting speed for TCT101-2ABC , if i have encoder in input?
1kHz or 10kHz?
Thank You!
What is max counting speed for TCT101-2ABC , if i have encoder in input?
1kHz or 10kHz?
Thank You!
-
- Moderatore
- Posts: 1671
- Joined: 29/10/2010, 10:09
- Contact:
Re: [TCT101-2ABC] with prescale value
Hi,
the maximum frequency for fase A+B is 100KHz.
the maximum frequency for fase A+B is 100KHz.
-
- Posts: 36
- Joined: 09/02/2011, 14:33
- Location: Latvia
- Contact:
Re: [TCT101-2ABC] with prescale value
Ciao!
How can i set prescale value for encoder that give 2000/round impulse and i need to show it in 360degree?
Prescale value is 5,55.
TCT101-2ABC?
It was something with inC1 and uiC1?
Thank You!
How can i set prescale value for encoder that give 2000/round impulse and i need to show it in 360degree?
Prescale value is 5,55.
TCT101-2ABC?
It was something with inC1 and uiC1?
Thank You!
-
- Moderatore
- Posts: 1671
- Joined: 29/10/2010, 10:09
- Contact:
Re: [TCT101-2ABC] with prescale value
With TCT101-2ABC you have to set:
inC1: "100"
uiC1: "16"
inC1: "100"
uiC1: "16"