[ATR142-ABC] Output relay after pre-programmed cycle ends

Post Reply
user497
Posts: 36
Joined: 09/02/2011, 14:33
Location: Latvia
Contact:

[ATR142-ABC] Output relay after pre-programmed cycle ends

Post by user497 »

Buongiorno!

Is there a controller from Pixsys, which can give a output signal, after the holding time ends? ( i mean pre-programmed cycle - i need output signal, when the time is over! )
Thank You in advance!
Pixsys tecnico 1
Moderatore
Posts: 1702
Joined: 29/10/2010, 10:09
Contact:

Re: Output related to the difference between AI1 and AI2

Post by Pixsys tecnico 1 »

Hi,
if you need to close a contact after a certain time (without monitoring any temperature), you can simply use a TCT101-1ABC or a ATR142 in timer-mode.
For more information visit our website to visualize the relative manuals.
user497
Posts: 36
Joined: 09/02/2011, 14:33
Location: Latvia
Contact:

Re: Output related to the difference between AI1 and AI2

Post by user497 »

Hello,

i need that output, after pre-programmed cycle ends! When controller reach the set point, it hold that temperature for holding time, that is already in controller, but after that holding time ends, we need other output signal, that process is ready!

Thank You!
Pixsys tecnico 1
Moderatore
Posts: 1702
Joined: 29/10/2010, 10:09
Contact:

Re: Output related to the difference between AI1 and AI2

Post by Pixsys tecnico 1 »

You can use an ATR142-ABC in "pre-programmed cycle" mode and set:

[AL.1]: "St.AL"
[A1.S.o]: "nc.S"

In this way the Q2 relay closes when the cycle ends or it is in stop.
user497
Posts: 36
Joined: 09/02/2011, 14:33
Location: Latvia
Contact:

Re: Output related to the difference between AI1 and AI2

Post by user497 »

Thank You!

I will test it! But i think, it will be ok!