Iris _

Pixsys Forum

everybody's effort for the same goal

Connecting the current sensor to the DDR244-13ABC-T

Post Reply
valik1979
Posts: 1
Joined: Yesterday, 17:27

Connecting the current sensor to the DDR244-13ABC-T

Post by valik1979 »

Hello, could you please tell me how to properly configure the input from the current transformer DDR244-13ABC-T. We used to use DRR245-21ABC, but it has been discontinued.
Pixsys tecnico 7
Moderatore
Posts: 138
Joined: 16/05/2024, 11:10

Re: Connecting the current sensor to the DDR244-13ABC-T

Post by Pixsys tecnico 7 »

Good Morning,
the current transformer (CT) need to be connected between the pins 18-19.

To configure the input you can look in the GROUP S - ct - Current Transformer of the DRR: here you will find all the parameters related to the current transformer.
parameter 287 ct F. Current Transformer Function is dedicated to the frequency of the input 50/60 Hz or DISAB.
parameter 288 ct v. Current Transformer Value is the scale of the current transformer.
ecc...

The instruction to set a heater break alarm are found in the chapter 7.8 of the manual.
I will leave a link that lea to a page where you can download the manual.
https://www.pixsys.net/regolatori-indic ... uti/drr244
Post Reply