 Post subject: false reading from TCT201-2ABC
PostPosted: 06/10/2020, 11:07 

Joined: 24/09/2019, 10:57
Posts: 1
Hello,
I used the TCT201-2ABC counter to read an input from a flow meter with aound 20 pulses per second.
By connecting the flowmeter to the counter and at the same time to a fast entry PLC I noticed that there is a big difference.
168 pulses in the PLC corresponds to 53 pulses in TCT201 although I put the input frequency (inF.1)to the maximum. I need to know if the counter has a frequency limit F <20HZ?


Top
Offline Profile  
 
 Post subject: Re: false reading from TCT201-2ABC
PostPosted: 07/10/2020, 9:21 
Moderatore

Joined: 12/09/2016, 14:49
Posts: 927
Hi,
the max frequency of the digitals input is 100Khz and there isn't limits for the min frequency.
How did you connect your digital input counting signal to TCT201-2ABC? Are you sure that by connecting the input together with your PLC there is no electrical noise interfering with the counting? Can you post the parameterization of your TCT201-2ABC and the electrical connections you have used?

Best regards.


Top
Offline Profile  
 
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC + 1 hour [ DST ]


Who is online

Users browsing this forum: No registered users and 2 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
Powered by phpBB © 2000, 2002, 2005, 2007 phpBB Group
Theme created StylerBB.net & kodeki