Evening all, first post and a query on the ATR 142 being used on a RO plant for Thermal disinfection every evening...
If controller is programmed at say 87oC and their is a power outage... how long will the controller retain its set point before it reverts to factory setting or does this not occur and controller retains its last setting..??
ATR 142 Memory after Power Failure
-
- Moderatore
- Posts: 1188
- Joined: 12/09/2016, 14:49
Re: ATR 142 Memory after Power Failure
Hi,
the value of the ATR142 Setpoint (and its parameters value) is stored in a EEPROM Memory. The EEPROM memory is not a Flash memory and the value is kept forever with power or not power suply actived.
Best Regards.
the value of the ATR142 Setpoint (and its parameters value) is stored in a EEPROM Memory. The EEPROM memory is not a Flash memory and the value is kept forever with power or not power suply actived.