DRR244-13ABC-T -- how to set relay 1 and 2

Post Reply
Davy
Posts: 2
Joined: 17/04/2023, 16:36
Location: FRANCE

DRR244-13ABC-T -- how to set relay 1 and 2

Post by Davy »

Dear Support

we got an DRR244-13ABC-T with Pt100 input.
We would like to have 2 relays, one NC and one NO.
We would like to set alarm value at 25°C.
when temperature is over 25°C, relay 1 should be open and relay 2 should be close.

the setting of input seems to work as we can read temperature.
we set in :
Group G
123 Ab.uP.A
126 N.c. St.
Group H
141 Ab.uP.A
144 N.o S.t

then when we change temperature, only relay 1 change is status .. not relay 2... why ?
kindly help

thanks and regards.
Davy.
Pixsys tecnico 6
Moderatore
Posts: 1184
Joined: 12/09/2016, 14:49

Re: DRR244-13ABC-T -- how to set relay 1 and 2

Post by Pixsys tecnico 6 »

Good morning,
Output Q1 is already enabled by default, so only output Q2 needs to be enabled from Par.123.
123 Ab.uP.A
126 N.o. St.
Parameters.jpg
Setpoint.jpg
Br
You do not have the required permissions to view the files attached to this post.
Davy
Posts: 2
Joined: 17/04/2023, 16:36
Location: FRANCE

Re: DRR244-13ABC-T -- how to set relay 1 and 2

Post by Davy »

Hi tecnico 6

thanks for your reply, we do :
35 c.01
123 up.dev
141 up.dev

Thanks for your answer.