Unable to activate Output1 in 4.20mA

Posted: 20/03/2019, 4:03
by ren973
Dear mrs, mr,
I am using a ATR234-20ABC.

This device is connected with a drew point sensor 2 wire 4.20mA
I can see the value on the controller .

But I need to transert this value with the Controller Output C1 in 4.20mA

My configuration is

2 - Sen {4.20}
3 - dP {0.0}
4 - LoLS {-100}
5 - uPLS {20}


1 - cout {c4.20}
67 rEtr {MA P}
68 LoLr {0}
69 UPLr {100}

jumpers are on JP5 an JP7 JP9 0-- (as picture 5.1.j)

The controller is unable to activate the C1 output
Is it a controller s problem ? configuration problem ?
Best regards
renaud

Re: Unable to activate Output1 in 4.20mA

Posted: 20/03/2019, 8:55
by Pixsys tecnico 6
Hi,
this is a configuration parameter issue: the parameter 1.[cout] must be "c.01" value if you want use the retransmission function. Please check it.

Best regards.

Re: Unable to activate Output1 in 4.20mA

Posted: 26/03/2019, 8:32
by ren973
Dear Mr
I changed the parameter as you said ... But still not working
C1 is still off

Best regards
renaud

Re: Unable to activate Output1 in 4.20mA

Posted: 26/03/2019, 9:18
by Pixsys tecnico 6
Hi,
parameters list and hardware configuration attached.
If it does not work fine using this settings, please contacts your reseller.

Best Regards.

Re: Unable to activate Output1 in 4.20mA

Posted: 26/03/2019, 9:48
by ren973
Thank you for your help