STR571 Help
-
- Posts: 1
- Joined: 06/06/2019, 23:35
STR571 Help
Hi, I have an STR571 device set up as a master which is connected to a humidity sensor slave and currently displaying values read from the sensor. I have a Modbus datalogger which can save values to a memory card and want to connect the datalogger as a slave device to the STR571. Is it possible to get the STR571 to write values to a slave device which are being read and displayed from another slave and if so how?
-
- Moderatore
- Posts: 1185
- Joined: 12/09/2016, 14:49
Re: STR571 Help
Hi,
It is not possible to get the STR571 to write values to a slave device which are being read and displayed from another slave, but you can use the STR571 COM2 port. The COM2 is a slave, so you can configure it by a Modbus Node Slave and you can read the Holding Register Modbus using an external Master device. If an external Master can write in to your datalogger, I think you can run your application. Please check Modbus Registers list available by STR571 user guide (paragraph number 10).
Best Regards.
It is not possible to get the STR571 to write values to a slave device which are being read and displayed from another slave, but you can use the STR571 COM2 port. The COM2 is a slave, so you can configure it by a Modbus Node Slave and you can read the Holding Register Modbus using an external Master device. If an external Master can write in to your datalogger, I think you can run your application. Please check Modbus Registers list available by STR571 user guide (paragraph number 10).