Pixsys Forum
https://forum.pixsys.net/

[TD410][TD710][TD810][TD820][PL500]Programming examples
https://forum.pixsys.net/viewtopic.php?f=25&t=2231
Page 1 of 1

Author:  Pixsys tecnico 6 [ 30/04/2019, 17:02 ]
Post subject:  [TD410][TD710][TD810][TD820][PL500]Programming examples

Programming examples for Movicon LogicLab and SCADA. These examples are for HMI series and PL500.

Before downloading the examples, we suggest to login to the website http://www.pixsys.net and to read the instructions for the HMI series, available at the following link:
https://www.pixsys.net/download_file.ph ... 8_RevD.pdf

EXAMPLE NO. 1: Read/Write Digital Outputs
This example shows sequential reading/writing or single activation of digital outputs on MCM260-1AD or MCM260X-1AD.
Attachment:
MODBUS_MCM260_1AD.zip

Attachment:
MODBUS_MCM260X_1AD.zip


EXAMPLE NO. 2: Read/Write Digital Outputs
This example shows sequential reading/writing or single activation of digital outputs on MCM260-1AD or MCM260X-1AD.
Attachment:
CAN_MCM260_1AD.zip

Attachment:
CAN_MCM260X_1AD.zip


EXAMPLE NO. 3: PID and Data Logger
This example shows the PID regulation with history records and graphic display of the data through I/O ETD-1644.
Attachment:
TD710_ETD1664.zip


EXAMPLE NO. 4: Dynamic Objects and Movicon Screens
This example shows how to handle dynamic objects within the screen according to the value of a variable. Also the example shows how to group several screens within a single screen using TAB.
Attachment:
Dinamic_object.zip


EXAMPLE NO. 5: Internal Movicon Report
This example shows how to handle an internal Movicon report and to save it in the project folder \DLOGGERS\.
Attachment:
Report_Interni_CE.zip


EXAMPLE NO. 6: LogicLab Mapping Modbus Slave Registers
This example shows how to make Modbus registers available by means of Ethernet using a PL500 as a slave.
Attachment:
Modscan32_TCP-IP.zip

Attachment:
PL500_tcp_ip.zip


EXAMPLE NO. 7: How to change the system time
This example shows how to change the system time of windows CE using a Movicon screen.
Attachment:
Cambio_ora_sistema_Rel_1_1.zip


EXAMPLE NO. 8: Movicon Trend Graphics
This example shows how to manage an XY trend (abscissa and ordinate variables sampled) and usual trends (abscissas on time base and ordinates with variables sampled).
Attachment:
Trend_XY.zip


EXAMPLE NO. 9: How to force page change from PLC
This example shows how to enable forcing a new page on Movicon using the PLC variables. Movicon cyclically performs a script to check if the forcing of the page change is enabled by the PLC. If the page changeover can be forced on the PLC, the screen changes in accordance with the value of a variable.
Attachment:
Forza_Cambio_Pagina.zip

Attachment:
EX09_user_guide.pdf


EXAMPLE NO. 10: Numerical Keyboard customization on Movicon
This example shows how to use an existing screen as "Numeric Pad" within a Movicon project. The screen has been optimized for use on TD410 and TD710, but it may also be used on other targets.
Attachment:
Numeric_Pad.zip

Attachment:
EX10_user_guide.pdf


EXAMPLE NO. 11: Pixsys GSM Module
This Function Block interfaces with the Pixsys GSM module (2200.20.002) and allows to send text messages (SMS) on events. The Function Block (see file attached SMS_ALERT.pll) must be imported into LogicLab using a special function of the "Project" menu -> "Import Objects".
For wiring and connection please refer to the enclosed user guide of the GSM module.
N.B.: In case of use with the serial port COM1 RS232, it is very important to use a standard RS232 cable with all signals RTS, CTS etc. (we suggest to use standard Belden cables).
Attachment:
SMS_ALERT.zip


EXAMPLE NO. 12: How to format SD Memory Expansion
Formatting an SD memory expansion. This guide shows how to handle an SD or microSD card to use it as data storing memory.
Attachment:
Rufus.zip

Attachment:
SD_Files.zip

Attachment:
EX12_user_guide.pdf


EXAMPLE NO. 13: Internet Explorer and Movicon
This example shows how to make your Movicon project available from remote for the Internet Explorer browser.
Attachment:
Banco_rele.zip

Attachment:
EX13_user_guide.pdf


EXAMPLE NO. 14: Configuration of MCM260X-9AD
This example shows how to configure I/O and probe reading of an MCM260X-9AD using Movicon on a TD710.
Attachment:
MCM260X-9AD_TD710_IO_Probe.zip


EXAMPLE NO. 15: Movicon Scheduler
This example shows how to use the object Movicon scheduler to activate a Boolean variable on weekly time bands.
Attachment:
Scheduler_Movicon_Rev_1_2.zip


EXAMPLE NO. 16: How to update or restore HMI and PL500
This guide shows how to use the DeviceFinder utility in order to upgrade or restore the default image of the device.
Attachment:
EX16_user_guide.pdf


EXAMPLE NO. 17: Graphic Interface Movicon HMI on remote PLC/HMI
This guide shows how to use the graphic Movicon interface of an HMI with another HMI or PLC of the same class of IP network addresses.
Attachment:
EX17_user_guide.pdf


EXAMPLE NO. 18: How to setting the Siemens S7 driver using a Pixsys HMI
This guide shows how to parameterize the S7TCP driver for the Siemens S7 PLC series, using only the Movicon graphical interface on the Pixsys HMI.
Attachment:
S7-TCP Driver Configuration for Pixsys HMI.pdf

Page 1 of 1 All times are UTC + 1 hour [ DST ]
Powered by phpBB © 2000, 2002, 2005, 2007 phpBB Group
http://www.phpbb.com/