User guide for editing and generating the Pixsys devices GSD file to import to Siemens TIA Portal/STEP7 and use with PROFIBUS PLCs:: how to make the MODBUS RTU registers of Pixsys PID Controller available on a Profibus network using the CNV510-PBUS-RTU-A device

1. Login to Download Area and check CNV510 Software, download and install "CNV510_PBUS_RTU_A_SW67561" software. Use the software to configure the CNV510-PBUS-RTU-A device and generating the GSD file.
https://cloud.pixsys.net/user-login.php
CNV510_Software_Download.png
If you want to configure a new GSD file, please refer to the step-by-step guide attached below, otherwise proceed to the next step to use pre-compiled GSD projects.
CNV510_PBUS_RTU_A.pdf
2.Extract and copy the contents of the following folders to the software installation location to make available examples of GSD file mapping:
Compositor_SW67561_projects.PNG
ATR244-12ABC-T
-Process Value
-Comand Setpoint available to read or write it
ATR244-12ABC-T.zip

DRR460-12A-T128
-Process Value
-Comand Setpoint available to read or write
DRR460-12A-T128.zip
MCM260X 1AD, 2AD, 3AD, 4AD
-Digital Input reading
-Digital Output writing
-Probe 1 process value
-Probe 2 process value
MCM260X-1_2_3_4-AD.zip
STR551-12ABC-T128R
-Process Value
-Totalizer value
-Alarm 1 and 2 value
-Reset Totalizer command available
STR551.zip
3. Use the software SW67561 to edit the GSD and add or remove Modbus registers or communication parameters.
NB for the Modbus registers list always refer to the user guide of the device.
STEP1: Rename or New project name.
STEP2: Set the PROFIBUS communication parameters. Use "Hardware with Ethernet" to enable the download project using the ethernet port of the CNV510-PBUS-RTU-A.
STEP3: Insetrt the Modbus Registers and slave node that you want to check.
STEP4: Save the XML file that you can use for the import by TIA Portal/STEP7 using the GSD file. Attention the file name may not exceed 12 characters.
STEP5: Download the device configuration using the Ethernet port.

4.Import the GSD file into TIA Portal and configure the module
TIA_Portal_Inport_GSD.png