Hello, I'm using a TD240 as a master device in a modbus network with VFDs as slave devices.
My customer wants to integrate the system to a PLC they already have but the PLC is a Master device in another modbus network. Is there a way i can communicate the TD240 as a master device with a 3rd party PLC as a master device too?
I also have a EPL101 that i can use as an interface if needed.
TD240 Master & Slave
-
- Moderatore
- Posts: 1185
- Joined: 12/09/2016, 14:49
Re: TD240 Master & Slave
Hi,
it is possible if you use the EXP1 as Master mode and COM2 as Slave mode, but you need use the RS232 for the COM2. Best Regards.
it is possible if you use the EXP1 as Master mode and COM2 as Slave mode, but you need use the RS232 for the COM2. Best Regards.