 Post subject: TD240 Master & Slave
PostPosted: 22/01/2019, 21:52 

Joined: 22/01/2019, 20:29
Posts: 3
Hello, I'm using a TD240 as a master device in a modbus network with VFDs as slave devices.
My customer wants to integrate the system to a PLC they already have but the PLC is a Master device in another modbus network. Is there a way i can communicate the TD240 as a master device with a 3rd party PLC as a master device too?
I also have a EPL101 that i can use as an interface if needed.


Top
Offline Profile  
 
 Post subject: Re: TD240 Master & Slave
PostPosted: 23/01/2019, 9:59 
Moderatore

Joined: 12/09/2016, 14:49
Posts: 645
Hi,
it is possible if you use the EXP1 as Master mode and COM2 as Slave mode, but you need use the RS232 for the COM2.
Attachment:
TD240_Master_Slave.PNG


Best Regards.