LAPTOP TO TD900 ETHERNET CONNECTION

Posted: 23/11/2015, 13:14
by user11915
Hi

I am trying to get my laptop to communicate with TD900 HMI panel.What is the procedure for setting IP addresses to communicate?

Re: LAPTOP TO TD900 ETHERNET CONNECTION

Posted: 23/11/2015, 14:10
by Pixsys tecnico 1
Hi,
set fixed IP address for both computers (not DHCP).
If you want to connect LogicLab/PageLab to TD900 HMI, you hsve to run LLExec.exe from "D:\LLExec\" before (TD900 HMI will become black).

Pagelab printing

Posted: 25/02/2016, 12:06
by user11915
I am having trouble printing from Pagelab. I want each page on a full A4 size sheet, i have tried changing the printer settings but it still remains very small on the top left side of the page.
How can i change the printer settings within pagelab?

Re: LAPTOP TO TD900 ETHERNET CONNECTION

Posted: 25/02/2016, 14:08
by Pixsys tecnico 1
Hi,
you can generate the documentation using this function
Cattura.JPG
Then you can go to the project's directory and in the folder "docImages" you will find all sinoptic's images at full resolution.

TD900 with two seperate Modbus networks.

Posted: 28/05/2019, 0:14
by gothomas
Hi,

I would like to setup a TD900 panel PC with two seperate Modbus Networks.

Do you have a setup procedure for it?

I know that the master is RTU on com 4, the second is Com 1 RS232 using an inverter from RS485 to Rs232.
Is this correct?

Will this allow me to increase the number of nodes that can be connected to the HMI?

Re: LAPTOP TO TD900 ETHERNET CONNECTION

Posted: 28/05/2019, 13:57
by Pixsys tecnico 6
Hi,
the TD900 hardware allows a single Modbus RTU Master. You can use the RS485 or the RS232 connection, but not both.

Best Regards.

Re: LAPTOP TO TD900 ETHERNET CONNECTION

Posted: 28/05/2019, 22:02
by gothomas
How is the Modbus TCP/IP setup?
it has a Generic Modus which im not sure about the set up procedure?
Do ye have the procedure for download?

Re: LAPTOP TO TD900 ETHERNET CONNECTION

Posted: 29/05/2019, 10:02
by Pixsys tecnico 6
Hi,
please check the example number 6 al follow link:

https://forum.pixsys.net/viewtopic.php?f=25&t=2231

It explains how to configure the "Status variable" and the Modbus TCP/IP using LogicLab software (same using TD900).

Best Regards.