[ATR401-22ABC-T] AO in Volt

Post by user2366 »

hello

i want to store the actual temperature via labview (5V). therefore i put the jumper on jp3. but then i only get 0.011 V altough the temperature is increasing.
any ideas?
Pixsys tecnico 1
Moderatore
Posts: 1662
Joined: 29/10/2010, 10:09
Contact:

Re: AO in Volt - ATR401-22ABC-T

Post by Pixsys tecnico 1 »

Hi,
if you want to retransmit the input signal in volt 0-10V, you have to set the following parameters:

[Sen] set the type of sensor
[rEtr] "Pro.1"
[LoLr] and [uPLr] as the lower and the upper limits for analog output for example:
Temperature form 0°C to 100°C --> 0V to 10V, [LoLr]:"0" and [uPLr]: "100"

You have also to put the jumper on jp3.
user2366
Posts: 6
Joined: 04/01/2012, 10:15

Re: AO in Volt - ATR401-22ABC-T

Post by user2366 »

thanks... works perfect!