This application allows to control a 2-flame burner with a single control setpoint (e.g. 250°C). The flames will ignite in sequence as the temperature drops and will go out above the control setpoint. The probe used is a PT100.

The parameters apply to an initial default situation. (password 9999 for instrument reset)
Control setpoint 250 °C
AL1 setpoint = 15°C (auxiliary intervention setpoint in deviation below the control setpoint)
Once the correct functioning of the burner has been verified, the end user can inhibit the setpoint of AL1 by setting the parameter P_70.[A.1.S.P.] = "hide". In this way the end user will display only the control setpoint, useful for water temperature control.

Operation:
Above 250°C flames off, contacts Q1 and Q2 open. (setpoint 1)
As the temperature drops:
A. 245°C = flame 1 lights, relay Q1 closes (5°C range settable by parameter P_20.[c.Hy.1])
B. 235 °C = flame 2 also ignites, relay Q2 closes (AL1 setpoint parameter, "control setpoint - AL1 setpoint = flame ignition 250-15=235).
Attachment:
atr144-abc_config.pdf

Attachment:
pixsys_atr144-abc_backup.zip

Best regards.


You do not have the required permissions to view the files attached to this post.


Top
Offline Profile  
 
Display posts from previous:  Sort by  
Post new topic This topic is locked, you cannot edit posts or make further replies.  [ 1 post ] 

All times are UTC + 1 hour [ DST ]


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
Powered by phpBB © 2000, 2002, 2005, 2007 phpBB Group
Theme created StylerBB.net & kodeki