Iris _

Pixsys Forum

everybody's effort for the same goal

[DDR245] 0-10v sensor and a digital input at the same time?

Post Reply
user13042
Posts: 3
Joined: 21/03/2016, 12:16

[DDR245] 0-10v sensor and a digital input at the same time?

Post by user13042 »

Hey,

I am trying to achieve a system where my DRR245 mirror's its sensor 0-10v:
If the sensor sees 10v the output on SSR should be 0v.
If the sensor sees 0v the output on SSR should be 10v.
If the sensor sees 6v the output on SSR should be 4v.

Except when on the digital input sees 10v. Then it shoud be:
If the sensor sees 10v the output on SSR should be 4v. <- NOT 0
If the sensor sees 0v the output on SSR should be 10v.

The mirroring without the digital input was doable with following parameters:
C.out : C.01
SEn : 0.10
rETr : vo.P
Lol.r : 10
uPLi.r: 0

What should i do to enable the functions I need so that i can make the digital input part work?
Pixsys tecnico 1
Moderatore
Posts: 1649
Joined: 29/10/2010, 10:09
Contact:

Re: [DDR245] 0-10v sensor and a digital input at the same ti

Post by Pixsys tecnico 1 »

Hi,
with digital input you can switch from automatic/manual mode.When you are in manual mode you can select, using the arrows, how much the anologue output must generate.
user13042
Posts: 3
Joined: 21/03/2016, 12:16

Re: [DDR245] 0-10v sensor and a digital input at the same ti

Post by user13042 »

Pixsys tecnico 1 wrote:Hi,
with digital input you can switch from automatic/manual mode.When you are in manual mode you can select, using the arrows, how much the anologue output must generate.
Thanks for your quick reply.

The digital input will switch values a lot of times during the day. Must i update the output percentage or will it remember the setting?

I put 10v on the digital input i go to manual mode, change the percentage so that SSR goes from 4-10. Then i put 0v on the digital input it will automatically change the percentage back to 100 so that SSR goes from 0-10. Then when i put 10v on it again it will have remember the percentage i put it on so that SSR changes to 4-10 again.

Is that correct?
Pixsys tecnico 1
Moderatore
Posts: 1649
Joined: 29/10/2010, 10:09
Contact:

Re: [DDR245] 0-10v sensor and a digital input at the same ti

Post by Pixsys tecnico 1 »

When you pass from automatic to manual, the regulatore mantains the last value, so if you have 7V on auto, when you pass to manual you will have 7V and then you can change using arrows.
HenryChind
Posts: 6
Joined: 03/02/2019, 19:08
Location: Sri Lanka
Contact:

DDR245 0 10v sensor and a digital input at the same time

Post by HenryChind »

When I open beta it auto finds my install directory and can load it no problems, except if you try to save in beta and play that save in the other one it will be odd.
Post Reply