We have the above unit operating with a PT100
SEn set to PtI
The relays operate at the correct temperature according to the display.
e.g. display =80 deg C
Relay prog to change at 80 deg C and the relay changes in line with the display.
The problem is that with a separate sensor (thermocouple) at the same location it is reading approx. 105 deg C
We have checked RTD
RTD wiring
and consider they are ok
Is there a reason for this type of offset??
[ATR121] ATR121-AD with PT100 reading error
-
Pixsys tecnico 1
- Moderatore
- Posts: 1738
- Joined: 29/10/2010, 10:09
- Contact:
Re: ATR121 AD
20 degrees is a really high value, I think it isn't a PT100B "Beta385"
-
user11605
- Posts: 3
- Joined: 20/07/2015, 15:13
Re: ATR121 AD
Not sure I understand the 20 degree ref as a high value.
Do you mean as a difference ?
Do you mean as a difference ?
-
Pixsys tecnico 1
- Moderatore
- Posts: 1738
- Joined: 29/10/2010, 10:09
- Contact:
Re: ATR121 AD
Yes, I mean as error in reading (difference between real and read).
-
user11605
- Posts: 3
- Joined: 20/07/2015, 15:13
Re: ATR121 AD
This is the spec for the RTD
Element: DIN IEC 751 Class B PT100 Probe:
316 stainless steel, 3mm or 6mm OD
Operating Range: -50 to +200°C
Cable construction: 3 core, FEP insulated Cable length:
2mtr standard
Element: DIN IEC 751 Class B PT100 Probe:
316 stainless steel, 3mm or 6mm OD
Operating Range: -50 to +200°C
Cable construction: 3 core, FEP insulated Cable length:
2mtr standard
-
Pixsys tecnico 1
- Moderatore
- Posts: 1738
- Joined: 29/10/2010, 10:09
- Contact:
Re: ATR121 AD
Hi,
disconnect the probe from the regulator and measure it with a multimeter.
At 105°C it must be about 140 Ohm. If it is about 130 Ohm the probe is reading 80°C so it is not working good.
Also check the cable you use: the three wires must have the same section and
electrical characteristics.
disconnect the probe from the regulator and measure it with a multimeter.
At 105°C it must be about 140 Ohm. If it is about 130 Ohm the probe is reading 80°C so it is not working good.
Also check the cable you use: the three wires must have the same section and
electrical characteristics.