 Post subject: [ATR121] ATR121-AD with PT100 reading error
PostPosted: 20/07/2015, 16:01 

Joined: 20/07/2015, 15:13
Posts: 3
We have the above unit operating with a PT100
SEn set to PtI
The relays operate at the correct temperature according to the display.
e.g. display =80 deg C
Relay prog to change at 80 deg C and the relay changes in line with the display.
The problem is that with a separate sensor (thermocouple) at the same location it is reading approx. 105 deg C
We have checked RTD
RTD wiring
and consider they are ok
Is there a reason for this type of offset??


Top
Offline Profile  
 
 Post subject: Re: ATR121 AD
PostPosted: 20/07/2015, 17:16 
Moderatore

Joined: 29/10/2010, 10:09
Posts: 1318
20 degrees is a really high value, I think it isn't a PT100B "Beta385"


Top
Offline Profile  
 
 Post subject: Re: ATR121 AD
PostPosted: 20/07/2015, 17:49 

Joined: 20/07/2015, 15:13
Posts: 3
Not sure I understand the 20 degree ref as a high value.
Do you mean as a difference ?


Top
Offline Profile  
 
 Post subject: Re: ATR121 AD
PostPosted: 21/07/2015, 8:39 
Moderatore

Joined: 29/10/2010, 10:09
Posts: 1318
Yes, I mean as error in reading (difference between real and read).


Top
Offline Profile  
 
 Post subject: Re: ATR121 AD
PostPosted: 21/07/2015, 9:05 

Joined: 20/07/2015, 15:13
Posts: 3
This is the spec for the RTD
Element: DIN IEC 751 Class B PT100 Probe:
316 stainless steel, 3mm or 6mm OD
Operating Range: -50 to +200°C
Cable construction: 3 core, FEP insulated Cable length:
2mtr standard


Top
Offline Profile  
 
 Post subject: Re: ATR121 AD
PostPosted: 21/07/2015, 9:39 
Moderatore

Joined: 29/10/2010, 10:09
Posts: 1318
Hi,
disconnect the probe from the regulator and measure it with a multimeter.
At 105°C it must be about 140 Ohm. If it is about 130 Ohm the probe is reading 80°C so it is not working good.

Also check the cable you use: the three wires must have the same section and
electrical characteristics.


Top
Offline Profile  
 
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 6 posts ] 

All times are UTC + 1 hour [ DST ]


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
Powered by phpBB © 2000, 2002, 2005, 2007 phpBB Group
Theme created StylerBB.net & kodeki