bonjour tous le monde
j'ai un probleme de connection de l'ordinateur et le plc TD 240

jai attache image de message d'erreur

voulez vous bien me guider a me connecter

NB: je suis nouveau dans le materiels pixsys

merci beaucoup
You do not have the required permissions to view the files attached to this post.
Pixsys tecnico 1
Moderatore
Posts: 1649
Joined: 29/10/2010, 10:09
Contact:

Re: Probleme connection with TD 240

Post by Pixsys tecnico 1 »

Hi,
PlProg doesn't recognize the PLC connect to the port com16. This error can caused because you have LabSoftView open with the memory card connect to the PC. Try to open only PlProg and connect only the TD240 to the pc; then re-click to the first line of the program line ("plc on COM16 PC).
user10989
Posts: 9
Joined: 16/04/2015, 13:59

Re: Probleme connection with TD 240

Post by user10989 »

Pixsys tecnico 1 wrote:Hi,
PlProg doesn't recognize the PLC connect to the port com16. This error can caused because you have LabSoftView open with the memory card connect to the PC. Try to open only PlProg and connect only the TD240 to the pc; then re-click to the first line of the program line ("plc on COM16 PC).

Hello,

I have a same problem with PlProg. I can not send program to PLC, but i have not LabSoftView. TD240-AD is connect to PC.
Help please
You do not have the required permissions to view the files attached to this post.
Pixsys tecnico 1
Moderatore
Posts: 1649
Joined: 29/10/2010, 10:09
Contact:

Re: [TD240] Probleme connection PlProg

Post by Pixsys tecnico 1 »

Hi,
are you using some serial converter USB-RSR232 or are you connecting directly from PC-DB8 RSR232 to the TD240?
Is the first time you try to connect with this PC to this TD240?
user10989
Posts: 9
Joined: 16/04/2015, 13:59

Re: [TD240] Probleme connection PlProg

Post by user10989 »

Pixsys tecnico 1 wrote:Hi,
are you using some serial converter USB-RSR232 or are you connecting directly from PC-DB8 RSR232 to the TD240?
Is the first time you try to connect with this PC to this TD240?
NO,i am using serial converter USB-RS485 with conector DB9. It is not first time.I was send program to PLC three times and it works, but now i cant send.
Pixsys tecnico 1
Moderatore
Posts: 1649
Joined: 29/10/2010, 10:09
Contact:

Re: [TD240] Probleme connection PlProg

Post by Pixsys tecnico 1 »

Try to connect to TD240 by clicking 1 time to:
1.png
.

Try to download program by using the function "PLC / PLC Maintenance / Update PLC firmware":
-Power-off TD240
-launch PLC update and during connection progress power-on TD240
You do not have the required permissions to view the files attached to this post.
user10989
Posts: 9
Joined: 16/04/2015, 13:59

Re: [TD240] Probleme connection PlProg

Post by user10989 »

Pixsys tecnico 1 wrote:Try to connect to TD240 by clicking 1 time to:
1.png
.

Try to download program by using the function "PLC / PLC Maintenance / Update PLC firmware":
-Power-off TD240
-launch PLC update and during connection progress power-on TD240
I can not resolve problem in this way. How i can restore TD240 on default ?
Pixsys tecnico 1
Moderatore
Posts: 1649
Joined: 29/10/2010, 10:09
Contact:

Re: [TD240] Probleme connection PlProg

Post by Pixsys tecnico 1 »

The procedure I describe is used to restore TD240.

I suggest you to connect using standard RS232 to COM2 (on DB9 or DB25, default serial port for programming).
user10989
Posts: 9
Joined: 16/04/2015, 13:59

Re: [TD240] Probleme connection PlProg

Post by user10989 »

Pixsys tecnico 1 wrote:The procedure I describe is used to restore TD240.

I suggest you to connect using standard RS232 to COM2 (on DB9 or DB25, default serial port for programming).
Thank you