[ATR401-22ABC-T] Error E-5 on display

Post Reply
user2366
Posts: 6
Joined: 04/01/2012, 10:15

[ATR401-22ABC-T] Error E-5 on display

Post by user2366 »

i have this error on display on power up.
i'm using a pixsys pt1000B. i tried it with 5 differnt pt1000s that i bought in the shop. (connection: white - 12, red - 13)
if i short the input the error is still on the display?
any ideas?
THX
Pixsys tecnico 1
Moderatore
Posts: 1662
Joined: 29/10/2010, 10:09
Contact:

Re: ATR401-22ABC-T: Error E-5 on display

Post by Pixsys tecnico 1 »

Hi,
You have to connect the probe on 12 and 13, set the [SEN.1] parameter as "Pt1K" and check if the [SEn.2] parameter is set as "diS."
user2366
Posts: 6
Joined: 04/01/2012, 10:15

Re: ATR401-22ABC-T: Error E-5 on display

Post by user2366 »

now it works.
i used the easyup code 2251 from the datasheet... any idea why it didn't work?
Pixsys tecnico 1
Moderatore
Posts: 1662
Joined: 29/10/2010, 10:09
Contact:

Re: ATR401-22ABC-T: Error E-5 on display

Post by Pixsys tecnico 1 »

Probably the [SEn.2] parameter wasn't set as "dis" so the controller check also the second input that was disconnected.